WATER CHEMISTRY Base water-quality specs on reality, not the GT OEM – Combined Cycle Journal

WATER CHEMISTRY Base water-quality specs on reality, not the GT OEM

Even if you don’t have a steam cycle, chances are your gas-turbine plant uses plenty of treated water—for evaporative cooling or inlet fogging, water/steam injection for NOx control and/or power augmentation, and possibly as the cooling medium for intercoolers if they are incorporated into engine design (Figs 1-3). The quality of this water is critical to minimize deposition and corrosion problems.

It is doubtful anyone would dispute the importance of maintaining strict treated water quality characteristics or of having a reliable water treatment, storage, and feed system. In many locations, emissions permits dictate that if the NOx injection steam/water isn’t available, neither is the plant. Unfortunately, much of this water cannot be recovered and recycled as it is lost to atmosphere through the GT exhaust.

However, Consultant David Addison, Thermal Chemistry Ltd, who serves users globally from company headquarters in New Zealand, raises the issue that many owner/operators find it difficult to comply with water-quality specifications generally issued by the GT OEM and the means of ensuring that they are met.

At the International Association for the Properties of Water and Steam (IAPWS) PCC Workshop, held in Moscow last year, he distinguished between the OEM water-quality guidelines—usually written to cover a range of gas turbines, fuels, and ambient environments worldwide—and what happens in practice. These guidelines (Table 1) may cause confusion among OEMs, A/E and EPC firms, and owner/operators.

Table 1: Typical water-quality guidelines provided by GT OEMs

Total suspended/dissolved solids………….<5 ppm
pH………………………………………….6 – 9
Conductivity at 25C………………………..<1.0 µS/cm
Silica………………………………………..<0.1 mg/L
Chloride/sulfate…………………………….<0.5 mg/L
Sodium/potassium*…………………………<0.2 mg/L
Particle size…………………………………~10 microns

* Includes contribution from fuel gas/oil

Addison lists the following reasons:

  • Total suspended solids (TSS) and total dissolved solids (TDS) are not aligned with particle-size and conductivity requirements because fuel may have contributed to the totals.
  • Technically, it’s extremely difficult to measure the pH of high-purity water with a conductivity of less than 5 µS/cm by online monitor or grab sample and analysis. Some OEMs require online pH monitors.
  • The contribution from carbonate is not normally accounted for in conductivity measurements.

Regarding the last point, keep in mind that while water at the outlet of the treatment plant/skid may meet or exceed the OEM’s conductivity specification, it immediately absorbs carbon dioxide after being transferred to the storage tank. CO2 in the air dissolves into the water and immediately ionizes to form carbonate ions, increasing conductivity and lowering pH (more acidic).

Inexpensive, inaccurate inline high-conductivity pH and conductivity analyzers typically are installed by the A/E or EPC at the outlet of the storage tank upstream of the GT. What’s more, the grab sample and analysis procedures are also not suitable for ultra-high-purity water.

The ensuing “drama” among all the actors involved, while project acceptance is delayed because the water specification cannot be met by testing at the site, is addressed by the following:

  • Attempts made to remove CO2 from the storage tanks, including nitrogen sparging and addition of CO2 scrubbers, fail and are abandoned.
  • Hundreds of grab samples are analyzed until one meets the OEM specs through luck rather than good science.
  • Eventually a degassed conductivity analyzer is installed following a cation exchange analyzer.

Typically, the degassed conductivity analyzer is a cation exchange analyzer modified such that the cation exchange resin has been removed, CO2 is eliminated via thermal degassing, and conductivity is re-measured (Fig 4).

IAPWS is considering a Technical Guidance Document (TGD) to address these gaps, although Addison enumerates the challenges, among them:

  • Water-quality specs from all of the vendors of water/steam-injected GTs is a huge data-gathering exercise.
  • Almost no attention is paid to water injection systems after initial plant commissioning.
  • Some GT OEMs have a strong desire for pH in the specification and it will be difficult to convince them that the required accuracy simply isn’t available.
  • Evaporative coolers using raw water would be very difficult to cover in such a document.

In the meantime, Addison suggests that a standard demineralized-water specification (Table 2) be considered by the OEMs. The changes address (1) that most of the problems arise from CO2 ingress and (2) that pH analyzers don’t have the necessary accuracy for this application, while keeping an allowance for contaminants from the fuel.

Table 2: Suggested revised water spec for GT OEMs

Degassed conductivity at 25C*…………..<1.0 µS/cm
Silica………………………………………<0.01 mg/L
Chloride/sulfate……………………………<0.002 mg/L
Sodium/potassium**………………………<0.002 mg/L
Particle size………………………………..~10 microns

* Online measurement; all others, grab sampling on routine basis
**Excludes contribution from fuel gas/oil